310.15(B)(6)
(6) 120/240-Volt, 3-Wire, Single-Phase Dwelling Services
and Feeders. For individual dwelling units of one
family, two-family, and multifamily dwellings, conductors,
as listed in Table 310.15(B)(6), shall be permitted as
120/240-volt, 3-wire, single-phase service-entrance conductors,
service lateral conductors, and feeder conductors
that serve as the main power feeder to each dwelling unit
and are installed in raceway or cable with or without an
equipment grounding conductor. For application of this section,
the main power feeder shall be the feeder(s) between
the main disconnect and the lighting and appliance branchcircuit
panelboards(s). The feeder conductors to a dwelling
unit shall not be required to have an allowable ampacity
rating greater than their service-entrance conductors. The
grounded conductor shall be permitted to be smaller than
the ungrounded conductors, provided the requirements of
215.2, 220.61, and 230.42 are met.