1. I have a 4160 VAC/ 480 VAC, 2000 KVA, delta- wye with neutral service transformer. Transformer secondary current is 2405 Amp. This transformer feeds a switchgear rated for 3000 Amp. The switchgear main breaker size is 3000 Amp.
2. I'm planning to install 8 - 600 MCM power cable per phase from transformer secondary to switchgear main. So, it will be a total of 24 - 600 MCM power cables from transformer secondary to switchgear main.
3. Question 1 - What is NEC recommended neutral conductor size from transformer secondary to switchgear main ? Would 8 - 600 MCM cables work for neutral ? Can you please confirm which NEC section is applicable for this scenario ?
4. The switchgear will have four 800 Amp breakers. Only one 800 Amp breaker has 1 phase, 277 V load. This 800 Amp breaker in switchgear feeds following two loads/ panels:
a) 3 Phase, 800 Amp, 480 V panel - I'm planning to install 2 sets of 600 MCM power cable from 800 Amp switchgear breaker to panel main breaker (rated for 800 Amp) and
b) 1 phase, 100 Amp, 277 V panel - What is NEC recommended cable size for this 1 phase, 100 Amp, 277 V panel (i.e) what cable size do I have to install from switchgear to this 1 phase, 100 Amp, 277 V panel ? Can you please confirm applicable NEC section for this scenario ? Do we need to run and install 2 sets of 600 MCM for neutral conductor or one set of AWG# 2 is acceptable ?
Thanks !
1. I have a 4160 VAC/ 480 VAC, 2000 KVA, delta- wye with neutral service transformer. Transformer secondary current is 2405 Amp. This transformer feeds a switchgear rated for 3000 Amp. The switchgear main breaker size is 3000 Amp.
2. I'm planning to install 8 - 600 MCM power cable per phase from transformer secondary to switchgear main. So, it will be a total of 24 - 600 MCM power cables from transformer secondary to switchgear main.
3. Question 1 - What is NEC recommended neutral conductor size from transformer secondary to switchgear main ? Would 8 - 600 MCM cables work for neutral ? Can you please confirm which NEC section is applicable for this scenario ?
4. The switchgear will have four 800 Amp breakers. Only one 800 Amp breaker has 1 phase, 277 V load. This 800 Amp breaker in switchgear feeds following two loads/ panels:
a) 3 Phase, 800 Amp, 480 V panel - I'm planning to install 2 sets of 600 MCM power cable from 800 Amp switchgear breaker to panel main breaker (rated for 800 Amp) and
b) 1 phase, 100 Amp, 277 V panel - What is NEC recommended cable size for this 1 phase, 100 Amp, 277 V panel (i.e) what cable size do I have to install from switchgear to this 1 phase, 100 Amp, 277 V panel ? Can you please confirm applicable NEC section for this scenario ? Do we need to run and install 2 sets of 600 MCM for neutral conductor or one set of AWG# 2 is acceptable ?
Thanks !