I know that you are allowed to calculate the neutral load for household cooking equipment (and dryers) using 70% (of the ungrounded load).
Does that mean that commercial cooking equipment(240v) is figured at 100% of the ungrounded for the neutral.
This would be for service calculations.
I've had people tell me that there is no neutral load for commercial cooking equipment (240v) and I tend to agree, but if that's the case then why the load for household calculations?