When I wore a younger mans clothes and did this every day this question was child's play but old brains don't work as well as younger ones 
400 amp 240/120 single phase service commercial building.
No load calculations have been made.
Service conductors will be parallel in one conduit.
220.61 allows the neutral to be sized at 200 amps + 70% of 200 amps or 340 amps,
Neutral is not considered to be current carrying (unbalanced load) so no fill adjustment required for neutral.
Question:
Since the neutral does not terminate on a device using 90deg conductors can the neutral be reduced to 3/0AL (175 X 2) or is it required to comply with the 75deg rating ?
400 amp 240/120 single phase service commercial building.
No load calculations have been made.
Service conductors will be parallel in one conduit.
220.61 allows the neutral to be sized at 200 amps + 70% of 200 amps or 340 amps,
Neutral is not considered to be current carrying (unbalanced load) so no fill adjustment required for neutral.
Question:
Since the neutral does not terminate on a device using 90deg conductors can the neutral be reduced to 3/0AL (175 X 2) or is it required to comply with the 75deg rating ?