It's been awhile since posting here and I am stumped on sizing overload protection for an air compressor motor and checking on an existing install by someone else.
Specs on motor:
230v
5 HP
Code: L
FLA: 21.5
Ph 1
Cont. Duty
SF: 1.15
SFA: 24.4
I am re-checking an installation done by an electrician of a motor running an air compressor. The 30 amp I/T CB keeps tripping literally 1 second after turning the breaker on due to the inrush current. I got a reading with my meter of amperage upwards around 120-130 before tripping out. This CB was installed at the compressor as the overload protection device.
I have used the code book to check the SC protection and came up with FLC of 28 amps based on 5 HP @ 230 volts. I multiplied 28 at 125% and came up with 35 amps. There is 10 awg THHN cu. and multiplied the 35 amps @ 250% and came up with 87.5 amps, protected by a 90 amp I/T CB. The SC protection is correctly installed by the previous electrician I believe.
I am stumped with the overload protection (part 3) on why the previous electrician used a 30 amp I/T CB.
I believe he took the FLA of 21.5 amps and multiplied that by 125% and got 26.87 amps. There is a 30 amp I/T CB as the overload protection which keeps tripping on inrush.
Would dual element time delay 30 amp fuses hold up better on inrush current than a 30 amp I/T CB?
I understand why SC protection using an inverse time CB would be sized @ 250% but cannot understand why it's permissible to be sized at 125% as overload when keeps tripping.
Any assistance would be greatly appreciated.
Thank you.
It's been awhile since posting here and I am stumped on sizing overload protection for an air compressor motor and checking on an existing install by someone else.
Specs on motor:
230v
5 HP
Code: L
FLA: 21.5
Ph 1
Cont. Duty
SF: 1.15
SFA: 24.4
I am re-checking an installation done by an electrician of a motor running an air compressor. The 30 amp I/T CB keeps tripping literally 1 second after turning the breaker on due to the inrush current. I got a reading with my meter of amperage upwards around 120-130 before tripping out. This CB was installed at the compressor as the overload protection device.
I have used the code book to check the SC protection and came up with FLC of 28 amps based on 5 HP @ 230 volts. I multiplied 28 at 125% and came up with 35 amps. There is 10 awg THHN cu. and multiplied the 35 amps @ 250% and came up with 87.5 amps, protected by a 90 amp I/T CB. The SC protection is correctly installed by the previous electrician I believe.
I am stumped with the overload protection (part 3) on why the previous electrician used a 30 amp I/T CB.
I believe he took the FLA of 21.5 amps and multiplied that by 125% and got 26.87 amps. There is a 30 amp I/T CB as the overload protection which keeps tripping on inrush.
Would dual element time delay 30 amp fuses hold up better on inrush current than a 30 amp I/T CB?
I understand why SC protection using an inverse time CB would be sized @ 250% but cannot understand why it's permissible to be sized at 125% as overload when keeps tripping.
Any assistance would be greatly appreciated.