I have been asked to help another electrician hook up a piece of equipment but the name plate doesn't have all the info I think I need. The equipment is a cooling unit for a container, I call it a "reefer" unit. The voltage required is 460V 3Ø and the only other info on the plate is LRA:77A.
I don't know how to determine the FLA with just that info. I can figure the OCP if I could get the FLA. Another thing is the voltage on-site is 240V/120V 3Ø. So I know it will require a transformer but can't order one until I can get the missing info. Is there a way to figure what's needed with this little info?
The equipment is used and the customer didn't get any info. I tried to look up the unit but didn't come up with anything.
I don't know how to determine the FLA with just that info. I can figure the OCP if I could get the FLA. Another thing is the voltage on-site is 240V/120V 3Ø. So I know it will require a transformer but can't order one until I can get the missing info. Is there a way to figure what's needed with this little info?
The equipment is used and the customer didn't get any info. I tried to look up the unit but didn't come up with anything.