Sizing OCPD and conductors of transformer that is oversized for secondary load

Status
Not open for further replies.
I have a 3PH 208V service. The equipment is rated at 3PH 480V 60A. I have a 75KVA 208V primary/480V secondary transformer that i already have in stock. My question is, can I size the 208V primary OCPD and corresponding conductors based off the calculated load of the equipment, or do I need to size the primary OCPD and conductors off of the 75KVA transformer?

So either my calculations would be:

75000 / 208 / 1.732 = 208.19 x 1.25 = 260.24 *sized based off transformer nameplate*

OR

60 x 480 x 1.732 = 49881.60 / 208 / 1.732 = 138.46 x 1.25 = 173.08 *sized based off secondary load nameplate*

If anyone can point me in the right direction or let me know if I have calculated anything incorrectly I'd appreciate it. Thanks for the help.
 
it tells you right in article 450.

Table 450.3(B) Maximum Rating or Setting of Overcurrent Protection for Transformers
10OO Volts and Less (as a Percentage of Transformer-Rated Current)...

The NEC is concerned with maximums, not minimums (in this case). You can do things at way UNDER their ratings if you so choose.

BUT, from a practicality standpoint, there are pitfalls. The primary OCPD, if under sized, may not hold in during initial inrush of the transformer when you first power it up. As a general rule then, I like to always size primary protection at the maximum allowable. Secondary... it makes no difference, you can do anything you like UNDER the maximum allowable.
 