I have a 3PH 208V service. The equipment is rated at 3PH 480V 60A. I have a 75KVA 208V primary/480V secondary transformer that i already have in stock. My question is, can I size the 208V primary OCPD and corresponding conductors based off the calculated load of the equipment, or do I need to size the primary OCPD and conductors off of the 75KVA transformer?
So either my calculations would be:
75000 / 208 / 1.732 = 208.19 x 1.25 = 260.24 *sized based off transformer nameplate*
OR
60 x 480 x 1.732 = 49881.60 / 208 / 1.732 = 138.46 x 1.25 = 173.08 *sized based off secondary load nameplate*
If anyone can point me in the right direction or let me know if I have calculated anything incorrectly I'd appreciate it. Thanks for the help.