Naterfrechette
New member
Hello I’m have a little confusion on selections an ocpd for a 100 amp continuous load. I know the code for 125% and it comes out to 125 amps. My wire size for 75 degrees would have to be a number 1 copper which is 130 amps. So my question is it a 125 amp breaker or size the breaker to wire at 130 and use a 150 amp per 240.B.? Any help would be great