hey guys when sizing an OCPD you do it with regards to the branch load not the power conductors right? (I may have this backwards).
for instance, I have a 3ph 25 horse @480 motor which draws 34A and I want to use a NEMA 2 starter with 50A thermal magnetic ckt breaker for protection. However I want to use #8 wire @90 deg C which is good for 55A.
that doesn't mean I now need to upsize my breaker to be over 55A does it? or that I would have to downsize my wire to #10 which is good for around 38A.
Thanks
for instance, I have a 3ph 25 horse @480 motor which draws 34A and I want to use a NEMA 2 starter with 50A thermal magnetic ckt breaker for protection. However I want to use #8 wire @90 deg C which is good for 55A.
that doesn't mean I now need to upsize my breaker to be over 55A does it? or that I would have to downsize my wire to #10 which is good for around 38A.