I am in the middle of installing a feeder circuit from an MCC to a panel that contains three separate VFDs. Each VFD will be controlling a 25HP motor (per drive). I am wanting to verify that my calculations are correct in sizing my main feeder breaker, wire size from MCC to panel, individual breakers in front of VFDs and wires going out to motor. Could someone please confirm that I have used the correct NEC rules?
1. Sizing Feeder Protection Device in the MCC:
Per NEC 430.52- For 25HP Motor- FLA= 34 Amps
34A*1.5= 51 Amps
Per NEC 430.62- 51A + 34A + 34A= 118 Amps
** So my protection device in the MCC would be 110 Amp Molded Case Breaker
2. Sizing Feeder Conductors from MCC to drive panel
Per NEC 430.24- (34A*1.25)+34A+34A= 110.5 A
Using THHN I would use #3 AWG since it is good for 115A
3. Sizing Circuit Breaker on Line Side of VFDs
Per NEC 430.52- For 25HP Motor FLA= 34 Amps
34A*1.5- 51A
So I would use a 50 Amp Circuit Breaker on the line side of each VFD.
4. Sizing Conductors from 50A Circuit Breaker to VFD and from VFD to Motor
Per NEC 430.122-
34A*1.25= 42.5A
So therefore #8 AWG conductors shall be used.
1. Sizing Feeder Protection Device in the MCC:
Per NEC 430.52- For 25HP Motor- FLA= 34 Amps
34A*1.5= 51 Amps
Per NEC 430.62- 51A + 34A + 34A= 118 Amps
** So my protection device in the MCC would be 110 Amp Molded Case Breaker
2. Sizing Feeder Conductors from MCC to drive panel
Per NEC 430.24- (34A*1.25)+34A+34A= 110.5 A
Using THHN I would use #3 AWG since it is good for 115A
3. Sizing Circuit Breaker on Line Side of VFDs
Per NEC 430.52- For 25HP Motor FLA= 34 Amps
34A*1.5- 51A
So I would use a 50 Amp Circuit Breaker on the line side of each VFD.
4. Sizing Conductors from 50A Circuit Breaker to VFD and from VFD to Motor
Per NEC 430.122-
34A*1.25= 42.5A
So therefore #8 AWG conductors shall be used.