I am having a problem understanding this exam question. Here is what is known and verified:
1. 75 degree terminations and use THWN
2. Feeder fed to 70Kva 480/208v transformer
3. Secondary supplies panelboard.
I calculated the following:
1. FLA to be 194A secondary output
2. Panel OCPD to be 175A to protect secondary output of 194a
The problem i run into is that I am told I should use a 2/0 (175a) to protect the secondary output. But, I came up with 3/0 (200a) when using the 10 ft. tap rule. Does anyone know if I only have to size this wire to the terminating OCPD in the panelboard and NOT size the wire for the larger 194A output on the secondary? I understand that the circuit should trip at 175A before overloading the secondary.
1. 75 degree terminations and use THWN
2. Feeder fed to 70Kva 480/208v transformer
3. Secondary supplies panelboard.
I calculated the following:
1. FLA to be 194A secondary output
2. Panel OCPD to be 175A to protect secondary output of 194a
The problem i run into is that I am told I should use a 2/0 (175a) to protect the secondary output. But, I came up with 3/0 (200a) when using the 10 ft. tap rule. Does anyone know if I only have to size this wire to the terminating OCPD in the panelboard and NOT size the wire for the larger 194A output on the secondary? I understand that the circuit should trip at 175A before overloading the secondary.