Sizing a wireway I'm pretty familiar with. My question I'm not too sure about is.

When splicing ina wireway with terminal blocks or Polaris taps does the formula change.

See the attached picture I'm thinking if I can add a set of three oughts for 200 amp solar service switch to this wireway.

It's a 10x10x48

9ec72f5805cb9e45f35e22891b8bae90.jpg


Sent from my SM-S906U using Tapatalk
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
The wireway fill is 20%, so I don't see fill as an issue. The installation in the picture may not be in compliance with 376.23(B), and even if it is, you will still have to be careful that your new conduit entries comply with that section.
The ground rod creates a 110.26(A) violation.
 