Curious if we will run into issues sizing an autotransformer to a motor FLA or does inrush need to be considered?
As an example, we will be using a 120/240p 16/32sec. If you run the calculation pulling 240 back 13.3% to 211V, a 5kva per the Acme tables shows the calculated amperage of 71A. The transformer will be oversized a touch for the actual load BUT inrush is something that may need considered... or maybe not? Is this already sort of worked out in the design of the transformer?
As an example, we will be using a 120/240p 16/32sec. If you run the calculation pulling 240 back 13.3% to 211V, a 5kva per the Acme tables shows the calculated amperage of 71A. The transformer will be oversized a touch for the actual load BUT inrush is something that may need considered... or maybe not? Is this already sort of worked out in the design of the transformer?