Sizing of bonding conductor

Status
Not open for further replies.

bluecollar84

Senior Member
Location
US
Hi where can I locate how to size properly my bonding conductor from the intersystem bonding termination to my telecommunications main grounding Busbar TMGB ? Thanks


Sent from my iPhone using Tapatalk
 
The plans show the locations of the telecommunications busbar but no sizing requirements for conductor sizing . Is it in the 2017 NEC anywhere ?


Sent from my iPhone using Tapatalk
 
The plans show the locations of the telecommunications busbar but no sizing requirements for conductor sizing . Is it in the 2017 NEC anywhere ?


Sent from my iPhone using Tapatalk

Article 800 - Communication Circuits

Specifically, 800.100(3)

No smaller than 14 AWG, no larger than 6 AWG. No specifics on how to arrive at what size to use.
 
3e32e73c45aadb6209b6c5a84ddfff32.jpg



Sent from my iPhone using Tapatalk
 
Status
Not open for further replies.
Top