Sizing of Conductors in Raceway

Status
Not open for further replies.

rd_cain

Member
With all of the various rules involved in grounding, I'm having a difficult time nailing this down. In a 3-phase 480 V application involving underground raceways, which rules do I use to size the grounded conductor (neutral) and the grounding conductor (ground) in the raceway.
 
Re: Sizing of Conductors in Raceway

You use Article 220 for the grounded conductor and Article 250 for the grounding conductor.
Don
 
Re: Sizing of Conductors in Raceway

Grounded Conductors
220.22 Feeder or Service Load, 250.24(B)(1) Routing and Sizing, 250.24(B)(2) Parallel Conductors.

Grounding Electrode Conductor (GEC)- Grounding Conductor 250.66

Equipment Grounding Conductor (EGC)
250.122

Pierre
 