Sizing of disconnect for ductless 24000 btu mini AC ?

Status
Not open for further replies.

edwalk1

Member
I was looking at the manual online before buying the unit and called service rep to get name plate information. No luck, I was going to put a 20a/2p breaker with a 20a fuse disconnect as that is what it seems to say in the manual. But after looking more I have found out that the starting current is 34 amps. I'm not sure if I should put in a 40amp disconnect to be safe.
 

Attachments

  • mansnap.JPG
    mansnap.JPG
    40.7 KB · Views: 0
  • ampdis.JPG
    ampdis.JPG
    82 KB · Views: 0

kwired

Electron manager
Location
NE Nebraska
20 amps is what you should install. If using fuses use time delay fuses or the 34 amp starting current that only lasts for a second or less may blow the fuse. An inverse time breaker will work with this starting current.
 