I have 2 production lines each with a non-continuous load of 1,000 amps and a continuous load of 300 amps.
If I run a main feed for 1,000 amps to a J Box and split it to (2) 500 amp disconnects and then use the disconnects to feed (2) 500 amp main breaker distribution panels, assuming all wiring is sized for the breakers. am I violating code?
Do I have to feed the line at the non-continuous load +%25 max load?
Does NEC care if I underfeed a device? Doesn't this overprotect the system or device?
Thanks,
Rich
If I run a main feed for 1,000 amps to a J Box and split it to (2) 500 amp disconnects and then use the disconnects to feed (2) 500 amp main breaker distribution panels, assuming all wiring is sized for the breakers. am I violating code?
Do I have to feed the line at the non-continuous load +%25 max load?
Does NEC care if I underfeed a device? Doesn't this overprotect the system or device?
Thanks,
Rich