Continous load X 1.25 + Non Continous load+ 25% of largest motor

Are we using the above rule to calculate (main feeder,main breaker,transformer,generator)?
 
That would be true for sizing the feeder (see 430.24).
The feeder short-circuit ground fault could be sized be 430.62.
Transformers and generators can get tricky especially if large motors are involved. Engineering and/or factory assistance plays a good role in those situations due to the different characteristics of motors such a LRA>
 