Sizing of MOP for Chiller with VFD

Status
Not open for further replies.

Zapp20

Member
Location
CT
I'm working on a chiller with a VFD and MCA is 1192 and MOP is 2000 amp. Trying to figure out how they got to the 2000 MOP.:?
 

GoldDigger

Moderator
Staff member
Location
Placerville, CA, USA
Occupation
Retired PV System Designer
Ignorant Brit strikes again........
MOP?
Short for MOCP, Maximum OverCurrent Protection.
Since the motor(s) all have overload protection the circuit OCP does not have to handle that, but the wiring of the device still needs short circuit and ground fault protection and the MO(C)P specifies what that needs to be. You can use smaller but risk nuisance trips.

Sent from my XT1585 using Tapatalk
 

Besoeker

Senior Member
Location
UK
Short for MOCP, Maximum OverCurrent Protection.
Since the motor(s) all have overload protection the circuit OCP does not have to handle that, but the wiring of the device still needs short circuit and ground fault protection and the MO(C)P specifies what that needs to be. You can use smaller but risk nuisance trips.

Sent from my XT1585 using Tapatalk
Thank you kindly sir.
 