Sizing of neutral for service

Status
Not open for further replies.

RIDGELY

Member
Need to know where in the code book it tells you how to size derate the neutral . What code article shows this infirmation ?
 
Take a look at 220.61, also keep in mind that the grounded conductor that is brought to the service must also meet the requirements of 250.24(C).

Chris
 
Status