We are getting ready to start a job and the Utility Transformer will be supplying the service with a 480/277 3phase 4wire system. This project doesn't have any 277volt loads. The feeder size is (4) sets of #350's for 1600amp. What is the minimum size I could use for the neutral conductor?
Also this job has an existing emergency generator that is to be rerouted to feed this new service. It does not have a neutral conductor in its raceway that I have to intercept and reroute to the new transfer switch. If there are no 277volt loads is there a need to install a neutral conductor in this existing raceway?
Also this job has an existing emergency generator that is to be rerouted to feed this new service. It does not have a neutral conductor in its raceway that I have to intercept and reroute to the new transfer switch. If there are no 277volt loads is there a need to install a neutral conductor in this existing raceway?