310.15(B)(2)(a) shows derating of parallel conductors, but not how to size them. For a 2000 kVa transformer with a 480V secondary I have 2406A. What size conductors would I use for two (or three) conductors on each phase?
Good afternoon, Bob. One possibility is you're building a large manufacturing facility, and the utility is providing 12.47 kV. You'll probably want a pair of outdoor transformers for that. I don't think you run 12.47 kV around to a handful of smaller transformers in that scenario. You might step down to, say, 480V and distribute *that* to a handful of smaller ones.petersonra said:Warning. Thread hijacking in progress.
Something I have often wondered.
Why is it that people even put in such huge transformers in the first place.
Why not scatter several smaller ones around the premises?
ramsy said:If there is no choice, there are single conductors for this load that may save some cost.
2500A F.Bus, PI.Bus, & CL.Bus are available in CU or AL.
My apologies for using those odd acronyms. some common amperages are listed below:kingpb said:I am not familiar with the F.Bus, PI.Bus ,and CL.Bus references. Could you expand.
Fuse Bus, Plug-In, Current-Limiting Bus
600 AL 800 1000
800 1000 1350
1000 1350 1600
1350 1600 2000
1600 2000 2500
2000 2500 3000
2500 3000 4000
3000 4000
4000 5000
5000