Sizing of service conductor from 100 amp. Main to a 125 amp. Load center main.

Status
Not open for further replies.
What is your rule in your area on how to treat the disconnect provided by POCO? Is it considered service disconnect or not?

Either way your 2/0 Al is more than 125 amp ampacity though, so it mostly comes down to whether there is large enough lugs or enough wire bending space on either end.
 