Scenario: In Philippines, we are using 3 single phase Transformer to have a 3 phase supply.
My supply will be Delta - Wye - 230 V 3 phase, 4 wires system. But my load is 4 Single phase loads which is causing me to unbalance load.
My question is,
1.) How to calculate for the size of transformer would it be the total kVA of the loads which is (4*18 kVA) = 72 kVA and use 3 - 25 kVA single phase transformer
or kVA = √3 x Line Voltage x Line Current = √3 x 230 x 234 = 93.2 kVA and use 3 - 37.5 kVA single phase transformer.
Please help. Thanks
Item | Description | Volts | Line Current A | Line Current B | Line Current C |
1 | 18 kVA Single Phase | 230 | 78 | 78 | |
2 | 18 kVA Single Phase | 230 | 78 | 78 | |
3 | 18 kVA Single Phase | 230 | 78 | 78 | |
4 | 18 kVA Single Phase | 230 | 78 | 78 | |
Total Feeder Current | 234 | 234 | 156 |
My question is,
Please help. Thanks