Have 3 parrallel runs of 75 degrees C rated, 350 kcmil in three parrallel runs of Emt. how would you figure out the maximum standard overcurrent device. My guess is you would need a 1000 amp?
Woudn't you round up to 1000 amp?
The OCPD would have to be 930 amps or less. You may be stuck with an 800 amp OCPD since 900 amps is not a standard size.