I recently installed some 10hp motors in a dry kiln. They are 10hp with a FLA of 13.9 and a service factor of 1.15. I used the 125% rule and got around 18amps. I rounded up to the next breaker size and arrived at 20amp. I had an issue with the breaker tripping and noticed my vendor sent me a type c breaker and I ordered a replacement breaker with a type D trip class. There is another electrician telling me that I need a 30amp breaker. I noticed that using a slide chart it will in fact recommend a 30amp circuit for a 10hp motor. I can’t however find anywhere in the NEC requiring one. What’s really going on here ? Who’s right ?