How should I size a panelboard coming from a 150 kW 240V/3-Phase high leg delta configured generator.
This system will provide power for various 240V/3-ph loads, as well as various 120/240V / 1-ph loads.
Load calculations say that 150 kW can provide 625 Amps at 120/240V / 1-ph
Also 150 kW is 360 Amps at 240V-3-ph
Would a 600 Amp three phase panelboard be sufficient to get the most out of this generator
This system will provide power for various 240V/3-ph loads, as well as various 120/240V / 1-ph loads.
Load calculations say that 150 kW can provide 625 Amps at 120/240V / 1-ph
Also 150 kW is 360 Amps at 240V-3-ph
Would a 600 Amp three phase panelboard be sufficient to get the most out of this generator