All,
I am sizing a panelboard (120/208V, 3ph) that has the following loads:
Phase A 25.5 kVA
Phase B 29.9 kVA
Phase C 23.4 kVA
My question is, do I size it based off the sum of the phases or average across the 3 phases:
Phase A+B+C = 78.8 kVA -> 219A load, 300A breaker, 400A frame
OR
(phase A+B+C)/3= 26kVA -> 73A, 90A breaker 100A frame
Most of the loads are single phase. There is only one piece of equipment that is 3 phase at 12kVA, and what is leading me to need clarification. The other problem is I only have access to 200A breakers to feed this.
Any information would be great.