melanconelectric
Member
- Location
- West Monroe, LA
Installed a 100KW Generac at a restaurant and ran 500 to it. Lugs from factory only for 400, Generac says MUST use those lugs on THAT breaker. Supplier says we may can get some crimp on studs that will lug into those lugs. Pull is only less than 30', cant I just re-pull with parallel sets? If so, how do you size parallels... 4/0? 300? 3/0?... is there a chart or table?
EXISTING: 3 #500 in 3 inch pvc (1PH)
EXISTING: 3 #500 in 3 inch pvc (1PH)