billdozier
Senior Member
- Location
- gulf coast
Hey guys can you point me in the right direction when it comes to sizing parellel feeds on a three phase 800a service. I know theres more than 310.16 that applies and thanks
infinity thanks for the code references. Now to make sure im on the right course. I see the code restrictions as how to run the conduit and wire. I also the reference to art. 250.122 which says I need a 1/0 cpr or 3/0 al egc wire. I also see the derating factor of 80% due to 4 current carrying conducters. Now how do I size the actual wire to feed this load. Thanks for the help. And am I tracting correctly?
Bill where are you getting the 4 CCC's from?
chris are you agreeing with me or am I still reading this wrong?
infinity three phase service blk red blu all cccs corect? Add neutral and you have 4 cccs correct?
I would not count the neutral, you don't have to.
For a building service it would be most unusual for the majority of the load to be non-linear.
I would not count the neutral, you don't have to.
For a building service it would be most unusual for the majority of the load to be non-linear.