1) Given the voltage/phase and MCA of a motor, how do you determine kVA (for panel schedule)?
2) How do you determine wire size?
3) How do you determing OCP? Per NEC 430.52 or just use MCA to mean "minimum circuit overcurrent protection ampacity"?
I'll try my hand at answering my own question, let me know how I do...
Voltage: 208/1.
MCA: 40
1) kVA = 40A*208V*sqrt(1)/1000 = 8.32 kVA
2) wire size is based on Table 310.16, 75C rated = #8 AWG Cu
3) OCP is 40A fuse in 60A switch. But what would breaker be sized? 40A?
2) How do you determine wire size?
3) How do you determing OCP? Per NEC 430.52 or just use MCA to mean "minimum circuit overcurrent protection ampacity"?