Sparky2791
Senior Member
- Location
- Northeast, PA
- Occupation
- Electrical Design
Do these open bottom polymer concrete boxes fall under the sizing requirements of NEC 314.28? Open bottom so U style pulls will be made inside the boxes.
So what you are 'saying' is the quazite box is classified as a handhole enclosure. The one thing that makes this tough is calcs are based on conduit rows. When they install conduits in these sometimes whey do not form a row.314.1 Scope.
This article covers the installation and use of all boxes and conduit bodies used as outlet, device, junction, or pull boxes, depending on their use, and handhole enclosures. Cast metal, sheet metal, nonmetallic, and other boxes such as FS, FD, and larger boxes are not classified as conduit bodies. This article also includes installation requirements for fittings used to join raceways and to connect raceways and cables to boxes and conduit bodies.
The only things I would worry about is the 6x between raceways that contain the same conductors, and the 6x to the opposite wall. You can apply the exception to the 6x from the opposite wall, but often that is not enough room for larger conductors in a hand hole...the exception is really aimed at conduit bodies.So what you are 'saying' is the quazite box is classified as a handhole enclosure. The one thing that makes this tough is calcs are based on conduit rows. When they install conduits in these sometimes whey do not form a row.