Sizing range and cooktop circuits

Status
Not open for further replies.

Vertex

Senior Member
When installing a range or cooktop (residential), I use the manufactures recommended circuit size found in the installation manual. When no manual is available, should I base the circuit on the nameplate rating or is it OK to base it on the load calculations from the 220 section of the NEC?
 
Vertex said:
When no manual is available, should I base the circuit on the nameplate rating or is it OK to base it on the load calculations from the 220 section of the NEC?

IMO you always go by the nameplate, the manuals tend to be generic.

Than with the nameplate info you at least provide a circuit that article 220 requires.
 
As Bob (iwire) said, start with nameplate rating.

You can then calculate the required ampacity of the circuit using the information in Table 220.55.

I provided some examples in Posts 21 and 29 at the following link. References are to the 2005 NEC.
http://forums.mikeholt.com/showthread.php?t=82561&page=3

If you are a glutton for punishing your mind, you can go through the whole thread.

There was a lot of discussion, but believe that in the end, the position that Table 220.55 may be used to calculate branch circuit requirements for a residential cooking appliance (range, or cook-top + wall-mounted oven) was sustained.
 
barbeer said:
Nameplate is good!:grin:

Yes, but!

If you put in a circuit based only on the nameplate rating of a 26 kW range, you will need a 110 Amp circuit.

If you use that 26 kW nameplate rating to find the circuit that is really required by Article 220.55 and Table 220.55, you will need only a 60 Amp circuit.
 
Bob NH said:
If you put in a circuit based only on the nameplate rating of a 26 kW range, you will need a 110 Amp circuit.

I sure would like to see a 26 KW household range.

And if the person can afford the kitchen that goes with that range I might sell them a 110 amp circuit. ;)

But I do agree with you about the .55 question. :)
 