To expand on that, the load referred to in 215.2 is the load as calculated per Article 220. Part IV would only apply to a feeder that is serving the "total connected load" of the residence. So a feeder to a subpanel carrying only part of the connected load would need to go by Part III.
Cheers, Wayne