Sizing Service Entrance Conductors - 2014 NEC

Status
Not open for further replies.

srbtrout

Inactive, Email Never Verified
Location
Woodland, WA USA
I am studying for the code calculations portion of my WA State Residential Administrator's exam (based on 2014 NEC).

When sizing service entrance conductors for a single family dwelling using either the standard or optional methods, which value of current do I multiply by 83%?

The calculated load (27600 volt-amps divided by 240 volts = 115 Amps?

or

The service rating determined by the next standard breaker size, 125 Amps?
 

ramsy

Roger Ruhle dba NoFixNoPay
Location
LA basin, CA
Occupation
Service Electrician 2020 NEC
The conductor is allowed to be sized 83% of the Main breaker.

..shall be permitted to have an ampacity not less than 83 percent of the (service or feeder) rating.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
Ramsy got it... If you have a 200 amp main breaker then the conductors feeding that 200 amp breaker can be sized at 166 amps (200 x .83) or larger.
 