I'm a bit confused on sizing service eq. Running 3 phase 480 volt loads with a 240 volt 1 phase service. Job specs. are
75 hp 3 ph. motor at 96 fla, VFD to run motor, 100 kva trans. stepping up 240v to 480v. (per load a 75 kva would be big enough)
96 x 1.73 x 2= 332 amps.1 ph.240 v.
Can the service be sized for the actual load? Does Nec require a 1.73 multiplier when sizing the service eq.?
Real world jobs out there pull 270 amps at the 1 phase 240 volt service with the same eq. plus a phase converter to run other loads. A 400 amp. service would be large enough.
Any references in the code book?
Thanks for your help.