Ran into a unique situation at a project. Customer sent in a load data sheet to the local utility before I got involved with the project. They had asked for at least 250 kVA for a new building, with room for expansion. The utility is installing another new service on site with a 500 kVA 12470V Delta Primary - 480Y/277 Wye-N Secondary pad mounted transformer ahead of the project. This is a large industrial park add-on. Customer now wants to have at least a 1200 amp 480v main panel with an 800 amp main for future expansion. I have never sized service equipment after the POCO has been involved and already sized the transformer. The utility transformer is good for 601 amps at 480v 3-phase, and I know they size differently than we do...and drive them over their ratings, buts that's always their call and risk. I am inclined to tell them to stick to 600 amps, which is still double their request and allows expansion. Has anyone dealt with this situation or have an opinion on what is the best option? Not sure about 800 amp main on 500 kVA utility from a liability standpoint, even if calculated load is well under that.