Transformer secondary to Main Breaker.
4 x 350KCM per phase (4 parallel feeds)
2 sets per conduit (2 x A, 2 x B, 2 x C, 1 x SSBJ in each conduit)
Using 250.102(C)(2) and Table 250.102(C)(1) Note 3, would I take the parallel set in one conduit (350KCM x 2 = 700KCM (i.e. Phase A plus Phase A in conduit 1)) to size the SSBJ or would I take the total of all phases (350 x 4 = 1400KCM (All Phase A's in both conduits)) to size the SSBJ? I believe it's the prior, but the note is not very clear.
4 x 350KCM per phase (4 parallel feeds)
2 sets per conduit (2 x A, 2 x B, 2 x C, 1 x SSBJ in each conduit)
Using 250.102(C)(2) and Table 250.102(C)(1) Note 3, would I take the parallel set in one conduit (350KCM x 2 = 700KCM (i.e. Phase A plus Phase A in conduit 1)) to size the SSBJ or would I take the total of all phases (350 x 4 = 1400KCM (All Phase A's in both conduits)) to size the SSBJ? I believe it's the prior, but the note is not very clear.