shortcircuit1
- USA
Hello,
I am trying to see if we have a standard method where we can calculate feeder size and OCPD. For example:
1.We have a IWH(Instant water heater).Its wattage is 7kW@208V. Now to calculate the feeder size all i do is 7000/208=33.65A. So i choose as per 310.15(B)(16) #10AWG. Now for OCPD since IWH is not a continuous load i can choose 35A breaker.But according to 240.4(D) i cant choose 35A OCPD because of small conductor rule.Am i right on this?
2.Lets say you have a cassette@208v and Running nominal amps=0.25 and an MCU(Mode changing unit)@208v and running nominal amps=0.4.I want to hookup both to the same circuit since the amp draw is minimal.So i added up the ampacities of the motors and 0.56A@208v i can put them on a 15A,2P circuit.Is this procedure right?
3.If you have a 5HP motor how do you convert that to kVA?(1HP=765w,so 5HP=3825W or 3.825kVA).But if i go to table 430.250(Full load current for three phase motors) if i see FLA of 5HP@208V it gives me 16.7A so to get kva=208*1.732*16.7=6.016kVA. Which method is right?