We are installing a new service transformer for some new equipment an industrial client is adding to their plant. We originally had some negotiations with the utility to oversize the transformer for some possible future loads and some possible load migrations. While we were in negotiations, schedule dictated that we needed to purchase the service switchboard, so we purchased a 3000A switchboard we thought would be large enough to feed anything they would supply. We originally thought 1500kVA would be the largest they would agree to supply. Turns out they had a 2000kVA they previously ordered and decided to use it for my application.
My question is it within NEC code to service a 2000kVA, 480/277V transformer with a 3000A switchboard with a 3000A MB. My concern is that 2000kVA/(480V * sqrt(3)) * 1000 * 1.25 = 3007A. Which is technically more than the bus rating. If we make sure never to overload the transformer is it within code to use the switchboard we already have purchased? The switchboard will feed various MCCs and the current loading will be around 650A (without diversity) and with future loading possibly going too 1200A total pending approval of future projects. I don't ever see this thing getting anywhere near fully loaded. I have seen example calcs online where they round of the 2000kVA fla to 2400 which makes the 1.25 multiplier come to an easy 3000A. Is my switchboard undersized for my transformer?
My question is it within NEC code to service a 2000kVA, 480/277V transformer with a 3000A switchboard with a 3000A MB. My concern is that 2000kVA/(480V * sqrt(3)) * 1000 * 1.25 = 3007A. Which is technically more than the bus rating. If we make sure never to overload the transformer is it within code to use the switchboard we already have purchased? The switchboard will feed various MCCs and the current loading will be around 650A (without diversity) and with future loading possibly going too 1200A total pending approval of future projects. I don't ever see this thing getting anywhere near fully loaded. I have seen example calcs online where they round of the 2000kVA fla to 2400 which makes the 1.25 multiplier come to an easy 3000A. Is my switchboard undersized for my transformer?
Last edited by a moderator: