I just wanted to make sure I was interpreting the code correctly.
I have a 240VAC line, that is protected by a 100Amp breaker. This line is a #2 CU conductor that was run thru conduit (115A per 310.15(b)(16)).
I wanted to tap this line in the middle, and bring the tap conductor to a 40A breaker, that feeds the new equipment loads.
The tap wire from the point where it would be tapped, to the 40A breaker is about 8 feet away.
Can I use 240.21(1) that applies to "Taps not over 3m Long"?
If so, I was planning on using a #8 cu. conductor for the wire from the point of tapping to the 40A breaker (50A per 310.15(b)(16).).
The tapped wire is planned to be run in square, plastic conduit, in a personnel restricted area.
I have a 240VAC line, that is protected by a 100Amp breaker. This line is a #2 CU conductor that was run thru conduit (115A per 310.15(b)(16)).
I wanted to tap this line in the middle, and bring the tap conductor to a 40A breaker, that feeds the new equipment loads.
The tap wire from the point where it would be tapped, to the 40A breaker is about 8 feet away.
Can I use 240.21(1) that applies to "Taps not over 3m Long"?
If so, I was planning on using a #8 cu. conductor for the wire from the point of tapping to the 40A breaker (50A per 310.15(b)(16).).
The tapped wire is planned to be run in square, plastic conduit, in a personnel restricted area.