dblake
Member
- Location
- Sacramento, CA, USA
Here is the existing setup. A feeder circuit supplies three branch circuits. Each branch supplies a 20 HP motor.
An engineering change to the process line is eliminating one of the branch circuits. Do I have to resize the feeder protection device in step 4, above?
- Each branch has a 27A FLC and a 70A SCPD (27 * 125% = 68).
- The feeder load is 87.75A (27*125% + 27 + 27).
- The feeder conductors are sized 3 AWG (100A for 75C wire at 30C ambient).
- The feeder conductors are protected with a 110A SCPD (<= 70 + 27 + 27 = 124).
An engineering change to the process line is eliminating one of the branch circuits. Do I have to resize the feeder protection device in step 4, above?
- Per NEC 430.62(A), must it now be downsized to 90A (<= 70 + 27 = 97)?
- Per NEC 430.62(B), can it now be sized "based on the ampacity of the feeder conductors"? If so, what is that basis?