OK, are you attaching the GES or EGC'S? That is the answer to your question. is
I know egc is equipment grounding conductor what's GES

Basically all our grounds come to this bar then we take 1 #6 wire to the rod from the bar so I'm talking about the ground coming to the bar from the neutral in each main switch essentially grounding the neutrals how do I size that wire ?
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
I know egc is equipment grounding conductor what's GES

Basically all our grounds come to this bar then we take 1 #6 wire to the rod from the bar so I'm talking about the ground coming to the bar from the neutral in each main switch essentially grounding the neutrals how do I size that wire ?
So is this bar where you ground the Service neutral in the service disconnect?
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
I know egc is equipment grounding conductor what's GES

Basically all our grounds come to this bar then we take 1 #6 wire to the rod from the bar so I'm talking about the ground coming to the bar from the neutral in each main switch essentially grounding the neutrals how do I size that wire ?
250.66
 