OK. The grounding electrode conductor must be sized based on the largest service-entrance conductor or equivalent area for parallel conductors in accordance with table 250.66.
What exactly does largest service-entrance conductor mean? Say for instance I had a small apartment house. It is getting two identical 100A panels installed in the basement side by side. #2 size ALU. SE cables for each panel. There is water pipe available for grounding electrode. The way I have been proceeding is to add the cir. mils. of two #2 ALU. The sum of these is the largest service-entrance conductor. So I would end up a #6 copper being barely big enough.
I have also heard the people argue that one #2 is the largest service-entrance conductor. In this instance a #6 cop would work either way you look at it.
What exactly does largest service-entrance conductor mean? Say for instance I had a small apartment house. It is getting two identical 100A panels installed in the basement side by side. #2 size ALU. SE cables for each panel. There is water pipe available for grounding electrode. The way I have been proceeding is to add the cir. mils. of two #2 ALU. The sum of these is the largest service-entrance conductor. So I would end up a #6 copper being barely big enough.
I have also heard the people argue that one #2 is the largest service-entrance conductor. In this instance a #6 cop would work either way you look at it.