The last part of Example D3(a) in Annex D of the 2005 NEC, under the heading "Feeder Neutral Conductor" states that when sizing the neutral [for this particular example] the entire lighting load must be considered the maximum imbalance. Since 210.11(B) does not apply to these buildings it cannot be assumed that the load will be evenly distributed.
The implication here is that if the load is calcultated on the basis of VA per square feet, it would be mandatory to evenly divide the load.
However, all of the examples in Annex D use the entire load as the maximum imbalance - even those computed on the basis of VA per square feet.
Any insights would be appreciated
Brian Dolan