I'm trying to determine the size of a 480V isolation transformer to feed an existing 250/500kW rated UPS. The isolation transformer is required because the existing 480V distribution system is being converted to an HRG system.
The information I have on the UPS show it as a 250/500kW rated UPS however it appears that it is supporting far less load than its rating based on the existing UPS feeder circuit. The existing feeder circuit consists of a 100A fused feeder and a 1/0 feeder cable. Based upon this feeder circuit this tells me that the UPS is limited to supporting just under approximately 100kW. The customer had also previously commented that he believes it supports 100kW worth of load.
In this situation would you size the isolation transformer for the 250kW rating of the UPS or just based upon the existing connected UPS load of 100kW? Would there be an issue of providing a 250kW rated transformer on the existing 100A feeder circuit in the event customer wanted to increase load in future and upgrade feeder circuit?
One thing about the UPS that has me a bit confused is that the bypass switch appears to have an overall 500kW rating but shows only a 250kW rating for the static switch. Is that common for the bypass switch to have an overall available frame rating with a lesser rated installed static switch (similar to breaker frame and trip unit as a comparison)? UPS is an APC UPS.
The information I have on the UPS show it as a 250/500kW rated UPS however it appears that it is supporting far less load than its rating based on the existing UPS feeder circuit. The existing feeder circuit consists of a 100A fused feeder and a 1/0 feeder cable. Based upon this feeder circuit this tells me that the UPS is limited to supporting just under approximately 100kW. The customer had also previously commented that he believes it supports 100kW worth of load.
In this situation would you size the isolation transformer for the 250kW rating of the UPS or just based upon the existing connected UPS load of 100kW? Would there be an issue of providing a 250kW rated transformer on the existing 100A feeder circuit in the event customer wanted to increase load in future and upgrade feeder circuit?
One thing about the UPS that has me a bit confused is that the bypass switch appears to have an overall 500kW rating but shows only a 250kW rating for the static switch. Is that common for the bypass switch to have an overall available frame rating with a lesser rated installed static switch (similar to breaker frame and trip unit as a comparison)? UPS is an APC UPS.