Sizing Transformer

Status
Not open for further replies.

isa7667

Member
Location
Paraguay
Hi there!

I need help to size a transformer that will be used in a supermarket.

According to my calculations, I get the following kVA:

To get these numbers I start measuring Amps for each item. The formulas are shown below:

kVA(1-Phase) = Volts * Amps / 1000
kVA(3-Phase) = Volts * Amps * sqrt(3) / 1000


where Volts: 220V (S. America)


The total Power is 552kVA. So I added an extra 20% and I get 663kVA.

What size of transformer do you recommend? Is it better to have 2 transformers with lower capacity or a big one? Will compressors in the system have to be considered for power correction? Thanks in advance for your support!

Details on Power Calculation:

ItemQtyPower/unitPower1-Phase3-Phase
Microwave112A12A2.64kVA
Fan10.5A0.5A0.11kVA
Ventilation12A2A0.88kVA
Scale Type140.3A1.2A0.264kVA
Scale Type211.5A1.5A0.33kVA
Hydraulic Press14A4A0.88kVA
PC11A1A0.22kVA
Kitchen Cutter13.5A3.5A0.77kVA
Scale Type310.3A0.3A0.066kVA
Packager31.5A4.5A0.99kVA
Meat Grinder12.5A2.5A0.953kVA
Meat Saw11.7A1.7A0.648kVA
Vacuum Packager17.5A7.5A1.65kVA
Checkouts185A90A19.8kVA
Server15A5A1.1kVA
Cooling Equipment1400A400A152.4kVA
Water Pump 114A4A1.52kVA
Water Pump 215A5A1.9kVA
Illumination1214.4A214.4A94.33kVA
AC Unit 360k BTU551.4A257A97.93kVA
AC Unit 500k BTU171.4A71.4A27.2kVA
AC Unit 18k BTU19.1A2A
Electrical Doors20.8A1.6A0.35kVA
Kitchen Equip 1Ph111.85A11.85A5.2KVA
Kitchen Equip 3Ph1362.7A362.7A138.2kVA
SUB TOTAL131.74KVA420.78kVA
TOTAL552.5kVA
 

kingpb

Senior Member
Location
SE USA as far as you can go
Occupation
Engineer, Registered
I would split up the loads on different panels. You certainly don't want to have lighting, receps, computers, scales, etc on a panel with motors and HVAC equipment.
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
Can you provide a bit more detail such as the utility supply voltage.
You show 3 phase equipment so hopefully you have a 3 phase supply. Can the large equipment not operate off the 3 phase supply (380 ? ).
Whichequipment actually needs the transformer ?

In many SA countries the only time you would need a transformer would be when you encountered 120v equipment.
 

isa7667

Member
Location
Paraguay
Can you provide a bit more detail such as the utility supply voltage.
You show 3 phase equipment so hopefully you have a 3 phase supply. Can the large equipment not operate off the 3 phase supply (380 ? ).
Whichequipment actually needs the transformer ?

In many SA countries the only time you would need a transformer would be when you encountered 120v equipment.

The incoming voltage is 23kV. The transformers steps this voltage to 3 lines of 220V at 50Hz. I have the option for 3 phase supply 380V and most of the larger equipments will be connected this way.

exmple.jpg

In terms of the calculation, when I use the formula kVA(3-phase) = V * A * sqrt (3) / 1000, do I use 380V as my Voltage?

For motors or compressors do I have to consider a special factor to adjust for startup?

Any other factors for equipment not running at the same time?

Thanks in advance!
 

kingpb

Senior Member
Location
SE USA as far as you can go
Occupation
Engineer, Registered
Thanks for the suggestion. Do you know what are the advantages and disadvantages of using a big unit instead of 2 smaller ones?

The advantage is that if you put lights on a panel with a bunch of 3-phase motors you could end up with light flicker. So in those terms you could put in two transformers; one at 380V 3ph, for your three phase loads, and another at 380Y/220V for everything else. Disadvantage is that you will pay more for initial installation with two transformers, and space could be a consideration.

My previous comment about 750kVA was based on std US sizes. Looks like your standard size in that range would be 630KVA. Take a look at your operating load diversity, the continuous load may be quite low in comparison to running load.
 