sizing transformer

Status
Not open for further replies.

brock1221

Member
Location
Alton, IL
I have a situation where I am trying to size the transformer based upon the load. Basically, I have two trailers one has two LTG Panels with 100A main breaker. The other trailer has one panel with a 100A breaker. I basically will utilize one single phase pole mounted transformer to feed into these two trailers. I was thinking 100 X 3 ==300A X 240V= 72kVA which equates to 80kVa transformer. Am I correct or wrong?
 

iwire

Moderator
Staff member
Location
Massachusetts
I have a situation where I am trying to size the transformer based upon the load.

But that is not what you seem to be doing. You seem to be sizing it by the breaker sizes. That will work but likely result in much larger transformer than really needed.


Basically, I have two trailers one has two LTG Panels with 100A main breaker. The other trailer has one panel with a 100A breaker. I basically will utilize one single phase pole mounted transformer to feed into these two trailers. I was thinking 100 X 3 ==300A X 240V= 72kVA which equates to 80kVa transformer. Am I correct or wrong?


I think the standard transformer sizes in that range would be 25, 37.5, 50, 75 or 100 kVA.

Are these pre-manufactured buildings or something like that?

If so the calculated load is often on a tag near the connection point.

BTW, running two feeders to one structure could be an issue. See part II of article 225, specifically '225.30 Number of Supplies'.
 

brock1221

Member
Location
Alton, IL
Any suggestions anyone...concerning the transformers kVA.. Am I right in the way I calculated it. BTW.. there will not be two feeders running into one building. One power feed will go to one trailer and another feed to the other one.
 

ActionDave

Chief Moderator
Staff member
Location
Durango, CO, 10 h 20 min from the winged horses.
Occupation
Licensed Electrician
Any suggestions anyone...concerning the transformers kVA.. Am I right in the way I calculated it. BTW.. there will not be two feeders running into one building. One power feed will go to one trailer and another feed to the other one.

You need to do a load calc for the trailers, al la Art. 220 or look for the tag that manufactured trailers have. If you do a load calc annex D is quite helpful. Just for comparison my whole house clacs out to 100A and pulls around 70A with every possible electric thing turned on.
 

kwired

Electron manager
Location
NE Nebraska
You need to do a load calc for the trailers, al la Art. 220 or look for the tag that manufactured trailers have. If you do a load calc annex D is quite helpful. Just for comparison my whole house clacs out to 100A and pulls around 70A with every possible electric thing turned on.

I don't know what my whole house calculation is, I do have electric water heater, 3 ton heat pump, 15 kW back up heat, electric range/dryer, well, plus shop (probably seldom exceeds 3-4000 VA, and when it does is for brief periods of time) - All that only supplied by 25 kVA transformer by the utility.
 

Besoeker

Senior Member
Location
UK
But that is not what you seem to be doing. You seem to be sizing it by the breaker sizes. That will work but likely result in much larger transformer than really needed.


I think the standard transformer sizes in that range would be 25, 37.5, 50, 75 or 100 kVA.
Just out of interest, can you get a 100kVA single ohase transformer as standard?
 

kwired

Electron manager
Location
NE Nebraska
Just out of interest, can you get a 100kVA single ohase transformer as standard?
Bob's link showed some pretty big transformers for single phase as being standard.

You will occasionally see 167 kVA as a POCO owned service transformer for single phase, especially for rural services. If you need more then that I think they generally want you to subscribe to three phase service. Most of what is around this area if you do need more then that you typically have a lot of motor load and would want three phase anyway.
 

Sahib

Senior Member
Location
India
You need to do a load calc for the trailers, al la Art. 220 or look for the tag that manufactured trailers have. If you do a load calc annex D is quite helpful. Just for comparison my whole house clacs out to 100A and pulls around 70A with every possible electric thing turned on.
There are two trailers and so application of demand factor is required for calculating optimum size of transformer. So OP better visit other similar installations to find out optimum size transformer at work unless the needed demand factor is made available to him.
 

iwire

Moderator
Staff member
Location
Massachusetts
There are two trailers and so application of demand factor is required for calculating optimum size of transformer. So OP better visit other similar installations to find out optimum size transformer at work unless the needed demand factor is made available to him.

The OP needs to follow the NEC, not the advice of those untrained NEC.
 
I have a situation where I am trying to size the transformer based upon the load.
I was thinking 100 X 3 ==300A X 240V= 72kVA which equates to 80kVa transformer. Am I correct or wrong?

iwire and the others are 100% correct here below. Don't just use 300A.

But that is not what you seem to be doing. You seem to be sizing it by the breaker sizes. That will work but likely result in much larger transformer than really needed.

I don't know what my whole house calculation is, I do have electric water heater, 3 ton heat pump, 15 kW back up heat, electric range/dryer, well, plus shop (probably seldom exceeds 3-4000 VA, and when it does is for brief periods of time) - All that only supplied by 25 kVA transformer by the utility.

You need to do a load calc for the trailers, al la Art. 220 or look for the tag that manufactured trailers have. If you do a load calc annex D is quite helpful.
Just for comparison my whole house clacs out to 100A and pulls around 70A with every possible electric thing turned on.

240 secondary but no mention of primary voltage.

You want to know the total load, meaning the electrical draw of both trailers when everything in them is turned on.
So like ActionDave said- for "around 70A", going by this chart in the link, kwired's 25kVA transformer is plenty for Dave's 70A.

And the price factor seems worse, if only going from 480V to 240V, the 100kVAs run nearly twice as much $$ as the 50kVAs and 3-4x the 25kVAs.
I can't think of any reason to pay 2-4x as much as necessary for....anything! ;)

http://1y18vt40uea231dp7l2g1lsi.wpengine.netdna-cdn.com/wp-content/uploads/SizingTransformers.pdf
 