What size of transformer would be correct for 6 x 1670w 120V
Step down transformer 480v 3PH. To 208/120V 3PH
Step down transformer 480v 3PH. To 208/120V 3PH
Is that because 10 kW isn't a standard transformer size for such transformers?
That would easier to answer if you provided your computation. But note that as the load is given in watts, we don't need any of the secondary or primary voltage info to size the transformer (or even know if the loads are 120V or 208V). And as there are 6 loads, they can be arranged in a balanced fashion. So the total load is a balanced 10,000 W (6 * 1,670W).I got 9.28 what did I do wrong?
I deleted my first post because I was going to re-post with the calculation but you beat me to it. As you've mentioned balanced I see this as 3340 watts on the A phase, 3340 watts on the B and 3340 watts on the C phase.But note that as the load is given in watts, we don't need any of the secondary or primary voltage info to size the transformer (or even know if the loads are 120V or 208V). And as there are 6 loads, they can be arranged in a balanced fashion. So the total load is a balanced 10,000 W (6 * 1,670W).
yesIs that because 10 kW isn't a standard transformer size for such transformers?
Because 10 kW would suffice for the load. [6 * 1,670 = 10,020, but 1,670 is surely only 3 significant figures, so the answer is 10,000.]
Cheers, Wayne