B Butler Member Jul 11, 2007 #1 What size transformer do I need if the primary voltage is 480 volts 3phase and the secondary will feed a 120/208 volt 3 phase 100 amp panel.
What size transformer do I need if the primary voltage is 480 volts 3phase and the secondary will feed a 120/208 volt 3 phase 100 amp panel.
C csanped411 Member Jul 11, 2007 #2 Butler said: What size transformer do I need if the primary voltage is 480 volts 3phase and the secondary will feed a 120/208 volt 3 phase 100 amp panel. Click to expand... Assuming the panel has a 100 AMP MCB: VA = [(100 A)x(208 V)x3^.5]/1.25 = 28,822 VA I would size a 480/277 - 208/120 30 KVA transformer.
Butler said: What size transformer do I need if the primary voltage is 480 volts 3phase and the secondary will feed a 120/208 volt 3 phase 100 amp panel. Click to expand... Assuming the panel has a 100 AMP MCB: VA = [(100 A)x(208 V)x3^.5]/1.25 = 28,822 VA I would size a 480/277 - 208/120 30 KVA transformer.
C csanped411 Member Jul 11, 2007 #4 Assuming the panel has a 100 A MCB: KVA = [(100 A)*(208 V)*3^.5]/(1000*1.25) = 28.83 KVA Transformer: 480/277 - 208/120 V, 30 KVA
Assuming the panel has a 100 A MCB: KVA = [(100 A)*(208 V)*3^.5]/(1000*1.25) = 28.83 KVA Transformer: 480/277 - 208/120 V, 30 KVA
B bcorbin Senior Member Jul 11, 2007 #7 I would size the transformer for the load fed, not the size of the panel, depending on the situation.
I would size the transformer for the load fed, not the size of the panel, depending on the situation.
V vinod Senior Member Location Saudi Arabia Jul 13, 2007 #8 what is 1.25 what is 1.25 U R absolutely correct Mr. Bcorbin.... KVA = [(100 A)*(208 V)*3^.5]/(1000*1.25) = 28.83 KVA In above formula What is 1.25? Last edited: Jul 13, 2007
what is 1.25 what is 1.25 U R absolutely correct Mr. Bcorbin.... KVA = [(100 A)*(208 V)*3^.5]/(1000*1.25) = 28.83 KVA In above formula What is 1.25?
C csanped411 Member Jul 13, 2007 #9 1.25 is 125%. I calculated the transformer KVA size based on the 100A main circuit breaker. The 100 A main circuit breaker rating is 125% of the panel load, based on amps. To size the 100 main circuit breaker I*1.25=100 AMP, I = 80 AMP.
1.25 is 125%. I calculated the transformer KVA size based on the 100A main circuit breaker. The 100 A main circuit breaker rating is 125% of the panel load, based on amps. To size the 100 main circuit breaker I*1.25=100 AMP, I = 80 AMP.